What is NEC's definition of a continuous load and how should it be treated in sizing?

Study for the Low Voltage Qualification Test. Explore flashcards and multiple-choice questions with hints and explanations for each, ensuring thorough preparation!

Multiple Choice

What is NEC's definition of a continuous load and how should it be treated in sizing?

Explanation:
Continuous load means a load that is expected to run for three hours or more. Because such loads can heat conductors and equipment over an extended period, NEC requires sizing the circuit to handle that heat by multiplying the continuous load by 1.25. In other words, circuits must be sized at 125% of the continuous load. For example, a continuous load of 40 A would require a circuit sized to at least 50 A (40 × 1.25). Loads that don’t run for three hours, or never run, don’t meet the definition of continuous and aren’t treated with this 125% factor.

Continuous load means a load that is expected to run for three hours or more. Because such loads can heat conductors and equipment over an extended period, NEC requires sizing the circuit to handle that heat by multiplying the continuous load by 1.25. In other words, circuits must be sized at 125% of the continuous load. For example, a continuous load of 40 A would require a circuit sized to at least 50 A (40 × 1.25). Loads that don’t run for three hours, or never run, don’t meet the definition of continuous and aren’t treated with this 125% factor.